Priups - 1kW real world test

Thread Tools
 
Search this Thread
 
  #21  
Old 07-25-2006, 07:32 PM
bwilson4web's Avatar
Engineering first
Thread Starter
Join Date: Oct 2005
Location: Huntsville, AL
Posts: 5,613
Wink Re: Priups - 1kW real world test

Originally Posted by wwu123
Here in northern California about 600 of those power pole-mounted transformers have failed in the past few days . . .

. . . and came back near nightfall to find the power still out and the PG&E folks waiting around for equipment and not promising power anytime soon. We then fully realized we'd have not even a fan to cool us down that night.

Now I'd actually bought a 800W inverter after reading old posts in the Yahoo Groups about using the Prius as a backup generator, since we often have outages during winter storms, but it had been a mild winter. So I skeptically pulled the box and instructions in the waning twilight, and opened up the trunk of my '02 Prius. In not even 5 minutes I had the inverter and an extension cord running into my house and powering a fan and a lamp. It was a piece of cake!

I did run into the "inrush" problem resetting the inverter when I plugged in a power strip that had a laser printer on it, so we didn't really try anything more than a couple of lamps and two table fans. But it's nice to know for future reference that I probably could've gotten our 5100 BTU window air conditioner working on it. Also just powering a few essential items, the motor hardly came on more than a few times that night to top off the battery.
. . .
I think someone hit it right on when they characterized it as a great solution for "camping out" at home. To power the entire house or even the refrigerator/TV reliably might take a greater effort and learning curve, but the inverter on the 12V battery is a <$100 solution that any novice can safely do in 5 minutes. Just having the ability to power a few devices at will - a lamp, a fan, a radio, a laptop computer - makes a tremendous difference in still feeling connected to civilization and not back in the Stone Age.
Well DONE!

Two things:

1) photos?
2) test your window AC at least once with the extension cord

Although my unit handles 1 kW with a 1.2 kW surge, I start by turning the AC thermostat to the warmest setting and the fan on low. Then I plug in the inverter. Once the fan is stable, then I turn down the thermostat to start the compressor. If your unit runs, you're probably OK although you'd like to monitor the compressor housing temperature to make sure it doesn't overhead. Do listen for any 'lugging' sounds.

If you can, test the circuit to see what the load measures and voltage to the AC.

Bob Wilson
 
  #22  
Old 07-26-2006, 08:16 PM
wwu123's Avatar
Enthusiast
Join Date: Mar 2006
Posts: 2
Default Re: Priups - 1kW real world test

Originally Posted by Mr Bean
What a great story. Would you mind telling what your specific model of inverter you bought? I think one of these days when car payments are not as fierce for me, I will pick up an inverter on the side.
For about $75 shipped off the Internet I bought a Motor Trend (probably not related to the magazine) 800W continuous / 1600W peak inverter. I think it's a modified sine wave inverter, and probably nothing particularly special about it except that it comes with a carrying case to hold the connectors and the instructions. Since I knew I would only be using mine on rare occasions, it was convenient to have the instructions and all the parts handy. Also I couldn't find one locally in the 800-1000W range, and I didn't want to go higher since some say there's a risk of fuse damage to the car above 1000W.

Originally Posted by bwilson4web
Well DONE!

Two things:

1) photos?
2) test your window AC at least once with the extension cord

Although my unit handles 1 kW with a 1.2 kW surge, I start by turning the AC thermostat to the warmest setting and the fan on low. Then I plug in the inverter. Once the fan is stable, then I turn down the thermostat to start the compressor. If your unit runs, you're probably OK although you'd like to monitor the compressor housing temperature to make sure it doesn't overhead. Do listen for any 'lugging' sounds.

If you can, test the circuit to see what the load measures and voltage to the AC.

Bob Wilson
No photos, since there's nothing special to see except that rectangular inverter sitting in the trunk and an extension cord running into the house. Amazing how simple it is.

No luck for me on the window AC though. I used a Watt-meter to measure the power draw. The fan on low was only 70W, turning it to cool with the thermostat high was the same since the compressor is still off. But when I slowly turn the thermostat down, the inverter tripped off right when the compressor kicks on. It seems the A/C wants 420W continuous, and more at the start.

My A/C is 5100 BTU, 9.0EER, 115V @ 5.3 Amps, about the same as yours. Seems like my inverter would be OK for the continuous load, but either the in-rush is too high or the inverter is just sensitive on the overload switch.

If I knew a different brand or model of inverter might be better with the surge, I might try another one. Would a 800VA computer UPS in-line smooth out the initial draw, or would it also trip off in the same manner? Well in any case, I can still power a lot of compact flourest bulbs and small electronics with what I have.
 
  #23  
Old 07-26-2006, 09:59 PM
bwilson4web's Avatar
Engineering first
Thread Starter
Join Date: Oct 2005
Location: Huntsville, AL
Posts: 5,613
Default Re: Priups - 1kW real world test

Originally Posted by wwu123
For about $75 shipped off the Internet I bought a Motor Trend (probably not related to the magazine) 800W continuous / 1600W peak inverter. I think it's a modified sine wave inverter, and probably nothing particularly special about it except that it comes with a carrying case to hold the connectors and the instructions. Since I knew I would only be using mine on rare occasions, it was convenient to have the instructions and all the parts handy. Also I couldn't find one locally in the 800-1000W range, and I didn't want to go higher since some say there's a risk of fuse damage to the car above 1000W.
One trick is to use a resistor network to bring the voltage to ~1 V and feed it into a PC line-input port. Use audio recording software, open source, to record signal and you can see what the voltage profile looks like. Piece of cake.

Originally Posted by wwu123
No photos, since there's nothing special to see except that rectangular inverter sitting in the trunk and an extension cord running into the house. Amazing how simple it is.

No luck for me on the window AC though. I used a Watt-meter to measure the power draw. The fan on low was only 70W, turning it to cool with the thermostat high was the same since the compressor is still off. But when I slowly turn the thermostat down, the inverter tripped off right when the compressor kicks on. It seems the A/C wants 420W continuous, and more at the start.

My A/C is 5100 BTU, 9.0EER, 115V @ 5.3 Amps, about the same as yours. Seems like my inverter would be OK for the continuous load, but either the in-rush is too high or the inverter is just sensitive on the overload switch.

If I knew a different brand or model of inverter might be better with the surge, I might try another one. Would a 800VA computer UPS in-line smooth out the initial draw, or would it also trip off in the same manner? Well in any case, I can still power a lot of compact flourest bulbs and small electronics with what I have.
I'm seeing ~700 W. load when running the AC, which is why I encouraged the test. The modified-sine wave appears to require more power than regular line power. Still, you have enough power for some nice box fans . . . or look for a 1 kW inverter with a reasonable surge.

The photo I was interested in was your connection to battery.You're looking at currents of a little over 60 A. and any input lead resistance will easily limit your power. I may have gone overboard but I really wanted to minimize the (I**2)R losses.

If you've got a small, space heater, you can use it for a straight resistive load. Then you can check the 12 VDC connections to make sure there is no heating or appreciable voltage drop. But then, there comes a point of 'polishing the musket *****.'

Sounds like you have a good solution. Have a happy!

Bob Wilson

ps. Swamp cooler?
 
  #24  
Old 12-21-2008, 05:39 PM
travelover's Avatar
Feral Engineer
Join Date: Jan 2007
Location: Detroit Area
Posts: 496
Default Re: Priups - 1kW real world test

I noticed that Costco has a 1000w / 1200 w surge inverter for $30 in the store. Pretty sweet price for a Xantrex.
 
  #25  
Old 12-23-2008, 09:07 AM
wwest's Avatar
Ridiculously Active Enthusiast
Join Date: Sep 2006
Location: Beautiful Pacific NW
Posts: 1,678
Default Re: Priups - 1kW real world test

A couple of CAUTION notes...

Capacitor start and capacitor run AC induction motors do not take "kindly" to MSW "square wave" power. Some will not start reliably, some will not start at all. This "effect" can be even worse for AC induction motors that drive refrigerant compressors, like that 5000BTU window air conditioner.

It takes 1666 watts to generate 5000BTU directly, say electric resistance heating. Air conditioners are typically 3-4 times more efficient ("heating" the great outdoors) so it would take about 400 watts to run that 5000BTU A/C. That would be GREAT if my story, caution note, ended there.

But it doesn't.

The starting, surge, inrush, load for an A/C is typically 2-3 times the running current, 800-1200 watts in this case. And that's only for an initial start cycle for an A/C compressor induction motor. Sequential "starts" are often with refrigerant head pressure, raising the starting surge to at least 3 times the running current, or more, depending on the type of thermostatic control is being used.

And....

These systems MUST somehow split the single incoming power phase into at least two phases, some only for induction motor startup, but others for the entire "run" duration. ALL of the phase splitting techniques are designed, optimized for sine wave power input. Some induction motors will not start at all with MSW inputs and many that do start will only start after many cycles of their internal overheating automatic resetting CB's.

With the advent of so many HM/RV owners using these MSW inverters the industry has wised up and is looking somewhat askance at honoring warranties for failures that appear mysterious....

120VAC @ 1000 watts from 12 volts = 90 amps....

From that tiny 12 volt lead-acid battery...?? And for more than 10 minutes...??

Are we leaving the key on so the DC-DC down-converter can be continually "recharging" the 12 volt battery from the hybrid..??

Basically any load device that doesn't directly provide HEAT or LIGHT (from HEAT) will be running on/with a completely out of line, out of the ordinary, PF, Power factor, and will likely overheat and possibly fail due to operating beyond the manufacturers design expectations. And by the way as the power factor goes "south" as a result of reactive loads/loading, the 1000 watt rating declines...and declines...and declines...

Go to RV.NET for more....
 

Last edited by wwest; 12-23-2008 at 09:16 AM.
  #26  
Old 12-23-2008, 09:19 AM
wwest's Avatar
Ridiculously Active Enthusiast
Join Date: Sep 2006
Location: Beautiful Pacific NW
Posts: 1,678
Default Re: Priups - 1kW real world test

Internal to these inverters is an DC-to-DC upconverter, via PWM and a voltage step-up transformer or system the 12 volts is upconverted to ~148 VDC. It would be much simpler if someone designed an inverter that used the hybrid battery voltage to begin with.
 
  #27  
Old 12-23-2008, 09:29 AM
wwest's Avatar
Ridiculously Active Enthusiast
Join Date: Sep 2006
Location: Beautiful Pacific NW
Posts: 1,678
Default Re: Priups - 1kW real world test

Originally Posted by Mr Bean
Not being an engineer, would someone in more basic technical terms explain what the goal being discussed in this thread is?

Am I correct in surmising that you all are using something called an inverter hooked to your Prius to use the Prius as a gas powered generator?
You are correct...

But the puzzling part is WHY...??

TONS cheaper, method vs purchasing a hybrid, would be to purchase two 6 volt deep cycle golf cart batteries to use in series, add a multiphase battery charger, and an inverter.

I would recommend a 3000 watt PSW, pure sine wave inverter.

Or $300 for a new briggs & Stratton or Honda powered 3500 watt genset.
 
  #28  
Old 12-23-2008, 01:18 PM
bwilson4web's Avatar
Engineering first
Thread Starter
Join Date: Oct 2005
Location: Huntsville, AL
Posts: 5,613
Default Re: Priups - 1kW real world test

The goal is to get a little more utility out of our Prius. Adding an inverter also provides AC power for laptops when going down the highway; and enough power to camp-out in one's home during a power outage.

Bob Wilson
 
  #29  
Old 12-26-2008, 09:31 AM
wwest's Avatar
Ridiculously Active Enthusiast
Join Date: Sep 2006
Location: Beautiful Pacific NW
Posts: 1,678
Default Re: Priups - 1kW real world test

Input....

Yesterday morning I got up to a cold and dark house and discovered our backup genset would start, but not pickup the load, and then shut down within about 30 seconds(***). While I was busy in and out of the COLD troubleshooting the problem my wife woke up and DEMANDED her morning coffee.

I have a spare car battery that I keep fully charged (always on a multi-phase charger) that I brought in, hooked an 800 watt MSW inverter, and plugged the coffee pot into that. I maybe got two cups brewed before the "beep-beep-beep" of the inverter started up, I had to "re-seat" the battery (spring) clamps and maybe got another cup brewed before the battery was below the tolerance of the inverter, 10.5 volts.

If a full size 12 volt car battery with HIGH starting current capacity cannot provide ~800 watts (~60 amps), for the 5-10 minutes it takes to brew a pot of coffee just how long will the 12 volt "low" current capacity supply more than 10.5 volts.

*** Intermittent spade-lug connection at the 10 amp regulator/field supply fuseholder.
 

Last edited by wwest; 12-26-2008 at 09:41 AM.
  #30  
Old 12-26-2008, 09:43 AM
wwest's Avatar
Ridiculously Active Enthusiast
Join Date: Sep 2006
Location: Beautiful Pacific NW
Posts: 1,678
Default Re: Priups - 1kW real world test

Originally Posted by bwilson4web
The goal is to get a little more utility out of our Prius. Adding an inverter also provides AC power for laptops when going down the highway; and enough power to camp-out in one's home during a power outage.

Bob Wilson
I would think it would be more productive to add an IR motion sensor to automatically turn on the Prius' headlights(***) and thereby illuminate your home's entry-way as visitors approach at night.





*** Provided, of course, the headlights are of the low wattage, 35W each, HID type.
 


Quick Reply: Priups - 1kW real world test


Contact Us -

  • Manage Preferences
  • Archive - Advertising - Cookie Policy - Privacy Statement - Terms of Service - Your Privacy Choices -

    When you click on links to various merchants on this site and make a purchase, this can result in this site earning a commission. Affiliate programs and affiliations include, but are not limited to, the eBay Partner Network.

    © 2024 MH Sub I, LLC dba Internet Brands


    All times are GMT -7. The time now is 11:44 AM.